@BruceM,
You nailed it ! Thanks.
I rewired to 120 volts and all noise and vibration disappeared.
If you look at the pictures above, the 4-prong 240 volt receptacle in the orange box now has two 20A, 120 volt receptacles.
Full load and still quiet. No vibration.
My house transfer switch requires split phase 240, so this generator will be mostly useless as a backup house generator.
Fortunately it powers the greenhouse 120vac electrical + heat loads, so it still has a job.
Hmmmm.... time for another generator build for the house ?
Now, here's a question for you (and anyone else).
The listeroid/ST-3 will be powering a greenhouse that is not grid connected.
It's electric outlets are not connected to the house, so they are not wired to a source that has ground and neutral bonded.
The ST-3 head has a floating neutral (not bonded to ground)
When powering the greenhouse, the whole system is a floating neutral.
When using the ST heads for home service the floating neutral is desired, but for powering anything other than a house, do we bond the ground with neutral? or not?
As a test, I made a plug which connects ground to neutral, and plugged it into the generator outlet while running. No observable change.
However, the safety aspect changed. For the better? or for the worse? I don't know.
Here's another (but similar) example:
A listeroid with ST head powering a 120 volt 75 amp (24 volt) battery charger for a large battery bank (1900 watts). No grid connection at all.
The charger is plugged directly in to a 120 outlet on the 120VAC ST head using standard 20A 120 volt plug with L1, Neutral, and Ground prongs.
Should the ground be connected to the neutral somewhere at the origin of the power ?
cheers