Hello folks! Merry Christmas to all!!
I have a question on my new Kohler 12RMO gen head. As received, it has a bonded neutral, so it would be appropriate to wire as a "Separately Derived System", meaning that the Neutral would need to be bonded at the generator AND the generator would require its own Equipment Grounding Electrode system. This is a les than ideal option for me.
This gen head is of the "Start-o-Matic family in that the gen head has the dynamo/starter windings included inside. Can/should those windings still be bonded to the case if I float the 120/240 neutral?
Has anyone out there un-bonded the neutral on their gen? If the Neutral is floating the system is now "Back-up power system and relies on the EGC system of the house/main panel. This would be more acceptable for my needs.
Thanks in advance!!