Lister ST2 with Brush 7KVA Generator
alexm:
Hi,
I've got a Lister ST2 with a Brush 7KVA Start-o-matic attached. I think I have attached a selenium rectifier?
If I change it to a modern equivalent rectifier is there some instructions somewhere for to do?
thanks,
Alex
ajaffa1:
Hi Alexm, welcome to the LEF. Yes that is an old selenium rectifier and it` over fifty years old. You will find two more in the control panel. The one you have photographed is actually a bridge rectifier and should be replaced with a modern silicon bridge rectifier something like this: https://www.ebay.com.au/itm/Durable-MDQ150A-150A-1600V-Full-Wave-Diode-Module-Single-Phase-Bridge-Rectifier/123151318385?epid=14019829297&hash=item1cac63fd71:g:5WkAAOSwqYZbBmAp
The new bridge rectifier will need to be mounted on a heat sink, a piece of 6 mm aluminium plate about 150 mm long by 50 mm wide should do nicely.
The two rectifiers in the control panel should be replaced with regular diodes.
Bob
alexm:
Hi Bob,
Thanks for the welcome!
It was actually made in 1978 but they made a lot with ST/SR model numbers stretching back to the sixties. It’s a single phase generator so I don’t think there any more rectifiers to worry about, is there? ???
Is there some way to tell which way to wire it?
Thanks,
Alex
dieselgman:
What make on the generator portion? We should have all the wiring schematics and parts listings.
dieselgman
ajaffa1:
Hi Alexm, the attached drawing should get you going.
I would recommend getting drawings and a service manual
Bob