Yes, agree, that particular example is very good, above a minimum load.
Using their figures.
In "search" mode, the standby current is 6 watts, or around 800mA at the nominal 48 volts.
Inverter overhead when running is around the 25 watts.... this is the voltage sense, mosfet drivers, gate current etc
At a 500 watt AC load .... a large lighting load using CFLs for an instance , 500/25 = 20 or around 80 percent efficiency, Pf =1, ie resistive load.
At 1500 watts , efficiency climbs to 1500/25, or close to their 90 percent.
With inductive or capacitive loads..... most given the proliferation of SMPS in almost all electronic devices, even including CFL lighting, the actual figures will be less, but close.
A period of low energy use, when sleeping for example, will see the lower efficiency over a longer time, perhaps say 8 hours in a 24 hr period. Higher cyclic loads during the day tend to be intermittent, refrigeration, microwave oven, kettle etc, therefore the higher efficiency periods occurs at random and for shorter periods.
So, the 500 watts drain over the 8 hour period will use 4 kilowatts, and a further 200 watts in "waste"
If the inverter then runs another 16 hours cycled between heavy and light at say a 50 percent duty cycle, another 8 hours can easily be spent running light, giving almost a half kilowatt in wasted consumption total over that 24 hours.
This is why an efficiency rating over time is far more informative in real life than an absolute "snapshot".figure.
I have always advocated using many smaller inverters for this reason, redundancy increases reliability, each inverter can be scaled to that one circuit, a large inverter that uses 20 watts overhead or more can then spent time either heavily loaded or not at all, where we can enjoy the lower 6 watts standby mentioned above.
Smaller inverters generally have less phantom overhead than larger types.... some as low as 50mA
This is all academic to many, but when off grid entirely, each watt costs from the battery bank and assumes greater value than an inferior cheaper version downloaded from the national grid.
A battery watt effectively requires another 5 to store it, given battery cycling depth issues, and to replace that watt takes almost an extra one given generator and chemical conversion losses at the bank.