Please forgive if you have already mentioned this, but have you flashed the field to check excitation voltage buildup? I think your symptoms appear to preclude a problem with field magnetism to start up generation. Your field voltage may be off to cause the low output though.
dieselgman
I *have not* done that. where can I learn about how to do that? starting to google now. how's this grab, with my further questions added?
To restore the small amount of residual magnetism necessary to begin voltage buildup, connect a 12 volt battery to the exciter field while the generator is at rest, as follows:
Remove exciter field leads F+ and F- from the voltage regulator. [where/what is this on the ST3K?]
CAUTION: Failure to remove the field leads from the regulator during flashing procedures may destroy the regulator.
Measure the exciter field resistance from the F+ to the F- lead. You should be able to read some resistance as you are measuring a continuous winding. An infinite resistance reading would indicate an open in the exciter field. Also check to be sure there is no path to ground.
Connect F+ to the positive pole of the battery.
Hold the F- lead by the insulated portion of the lead wire, touch F- to the negative pole of the battery for about 5 to 10 seconds, then remove.
Reconnect F+ and F- to the regulator. Repeat the procedure if the generator fails to build voltage.