Author Topic: ST-15 flicker reduction with flywheel (question)  (Read 11699 times)

cujet

  • Hero Member
  • *****
  • Posts: 960
  • Lister power rules!
    • View Profile
    • www.cujet.com
ST-15 flicker reduction with flywheel (question)
« on: August 31, 2011, 11:14:38 PM »
My 20/2 'roid drives a 23.3 inch flywheel at 850RPM (de-rated from 1000RPM). The ST-15 generator head has a very cool "Mike Montieth" heavy pulley. That pulley can accept a "bolt on" flywheel to reduce flicker.

So my question is this: How much flywheel do I need on the ST head to significantly reduce flicker? I believe Mike said he can make me a 16 inch flywheel that's 2 inches thick as that's the size that fits my application.

If you look carefully, you will see that the pulley also has a smaller diameter that allows me to run the engine at 600RPM for lower output and lower fuel consumption.


People who count on their fingers should maintain a discreet silence

piperpilot3tk

  • Full Member
  • ***
  • Posts: 195
    • View Profile
Re: ST-15 flicker reduction with flywheel (question)
« Reply #1 on: September 01, 2011, 12:03:35 AM »
Chris, I don't know how much mass it would take to do the trick, or if it will even completely eliminate the flicker, however I think the large bearings of the ST-15 will support more of a shaft load than you are probably able to fit to it.  So if it were me I would go big or go home  :D

ronmar

  • Hero Member
  • *****
  • Posts: 1227
    • View Profile
Re: ST-15 flicker reduction with flywheel (question)
« Reply #2 on: September 01, 2011, 01:15:25 AM »
The problem you are going to start running into is the transmission of energy from the flywheel to the generator.  That added mass will also increase the generator head's reluctance to increase in RPM during the power stroke.  At some point, the belt is going to be unable to deal with the load being applied during the power stroke.

I have thought about experimenting with flicker points, but just havn't got around to doing it.  Some older single cylinder gensets used these to switch a little added resistance into the field circuit during the power stroke, to "take the edge off" of the output voltage during the acceleration of the power stroke.  It should be pretty easy to drive a set of contacts off of the cam on a single.  A twin would be a little trickier as both ends of the cam are used, but I think a delay circuit could be used in conjunction with the intake tappets to provide a more level voltage output... 
PS 6/1 - ST-5.

Tom

  • Hero Member
  • *****
  • Posts: 1746
  • Green power is good.
    • View Profile
Re: ST-15 flicker reduction with flywheel (question)
« Reply #3 on: September 01, 2011, 01:26:08 AM »
IIRC a SOM has a 150 lb weight on the gen head. Perhaps Mike could make you a set of nesting flywheel plates that weigh around 50 lbs ea so that you could add and remove weight to determine the optimum weight.
Tom
2004 Ashwamegh 6/1 #217 - ST5 just over 3k hours.

38ac

  • Hero Member
  • *****
  • Posts: 2327
    • View Profile
Re: ST-15 flicker reduction with flywheel (question)
« Reply #4 on: September 01, 2011, 03:05:56 AM »
You may also want to consider smoothing out the power pulses with added weight to the crankshaft. On the originals Lister used both. As Ronmar said at some point adding weight to the gen head shaft is going to be a strain on the drive belt. I have a twin myself. The original thought was having two cylinders the flicker problem would be much less, duh! And I knew about the uneven firing too. I believe that the twins are actualy worse than the singles all other things being equal. Good luck!
Collector and horder of about anything diesel

dieselgman

  • Hero Member
  • *****
  • Posts: 3189
    • View Profile
    • Lister Parts
Re: ST-15 flicker reduction with flywheel (question)
« Reply #5 on: September 01, 2011, 03:32:40 AM »
I don't know if Lister ever sanctioned it but I have seen multiple flywheels (3 and 4) installed on CS models before. That should stabilize things a bit once it is up to speed, maybe. Not sure how much improvement that might make. Has anyone out there tried this out?

dieselgman
ALL Things Lister/Petter - Americas
Lyons Kansas warehousing and rebuild operations

Horsepoor

  • Sr. Member
  • ****
  • Posts: 250
  • West Palm Beach, Florida
    • View Profile
Re: ST-15 flicker reduction with flywheel (question)
« Reply #6 on: September 01, 2011, 07:08:56 AM »
Chris,

I have an extra, non spoked, flywheel free to a good home if you want to try it. It is in good shape and left over when I added the PowerAna electric start kit. Do you want to try it?

Incidentally, wow, great photo, what a chick magnet....
« Last Edit: September 01, 2011, 07:11:50 AM by Horsepoor »
GTC 20/2 down rated to 850 rpm - ST 15
Metro 6/1 800 rpm on cart - ST 7.5

toydiesel01

  • Full Member
  • ***
  • Posts: 101
    • View Profile
Re: ST-15 flicker reduction with flywheel (question)
« Reply #7 on: September 01, 2011, 02:26:16 PM »
I have been toying with the idear of adding a small cap to the gens out put to help take the edge off.
Will this work????

ronmar

  • Hero Member
  • *****
  • Posts: 1227
    • View Profile
Re: ST-15 flicker reduction with flywheel (question)
« Reply #8 on: September 01, 2011, 02:56:50 PM »
I have been toying with the idear of adding a small cap to the gens out put to help take the edge off.
Will this work????
No!

It would work to stabelize a DC voltage, but not an AC one...
PS 6/1 - ST-5.

piperpilot3tk

  • Full Member
  • ***
  • Posts: 195
    • View Profile
Re: ST-15 flicker reduction with flywheel (question)
« Reply #9 on: September 01, 2011, 07:06:04 PM »
Horsepoor, if Chris does not want that extra flywheel I would LOVE to have it. 

bschwartz

  • Sr. Member
  • ****
  • Posts: 323
    • View Profile
Re: ST-15 flicker reduction with flywheel (question)
« Reply #10 on: September 01, 2011, 08:02:27 PM »
   "....It would work to stabelize a DC voltage, but not an AC one..."

But isn't it a fluctuating DC in the Z winding that then causes the poor AC?
If so, could the capacitor be put in line (actually parallel I think) with the Z?
-Brett

1982 300SD, 1995 Suburban 6.5, 1994 F250, R170, Metro 6/ sold :( , Witte CD-12 ..... What else can I run on WVO?

Tom

  • Hero Member
  • *****
  • Posts: 1746
  • Green power is good.
    • View Profile
Re: ST-15 flicker reduction with flywheel (question)
« Reply #11 on: September 01, 2011, 11:49:21 PM »
Brett, he's changed to an AVR that runs on a 120v ac leg. That completely eliminates the z winding from the system. The only issues left should be mechanical.
Tom
2004 Ashwamegh 6/1 #217 - ST5 just over 3k hours.

bschwartz

  • Sr. Member
  • ****
  • Posts: 323
    • View Profile
Re: ST-15 flicker reduction with flywheel (question)
« Reply #12 on: September 02, 2011, 02:20:07 AM »
The AVRs I got from Tom still used the Z winding, but the AVR regulated the output.
What model AVR does Tom sell that eliminates the Z winding all together? 
-Brett

1982 300SD, 1995 Suburban 6.5, 1994 F250, R170, Metro 6/ sold :( , Witte CD-12 ..... What else can I run on WVO?

Startomatic

  • Jr. Member
  • **
  • Posts: 86
    • View Profile
Re: ST-15 flicker reduction with flywheel (question)
« Reply #13 on: September 02, 2011, 06:22:08 AM »
i attached a Kubota 5hp donor flywheel that i had. with the engine running at 630 rpm, the additional flywheel on the ST5 eliminate the flicker totally.

however, the belting now "kick.kick.kick" on every firing stroke. i guess i have to live with it.

my Vbelt is on un-groove flywheel on the engine end.



the grey pulley was the original drive for the radiator fan. was now thinking to piggy ride a automotive alternator with it to charge battery.
Lister 6/1 with ST5,Lister SL3, JP1
Yanmar Diesel L10,TS65,TS105 with Interpump hp head
Yanmar 3TN72, NT110 with ST5
Andoria S320
Kubota Z400 Twin Diesel with KEW 1500 hp head
Isuzu 25KVA Diesel silenced Genset
ChangChai EV80
JianDong 1115
Shineray250 watercooled- gasoline
ListerHRW3water

ronmar

  • Hero Member
  • *****
  • Posts: 1227
    • View Profile
Re: ST-15 flicker reduction with flywheel (question)
« Reply #14 on: September 02, 2011, 03:33:17 PM »
  "....It would work to stabelize a DC voltage, but not an AC one..."

But isn't it a fluctuating DC in the Z winding that then causes the poor AC?
If so, could the capacitor be put in line (actually parallel I think) with the Z?

The Z winding generates the energy used by the field. it is AC, and goes thru a diode rectifier to make unfiiltered DC to be fed back into the field.  The Z winding generates energy based on 2 factors.  Generator load, and generator RPM, so the voltage output is partially RPM dependent.  The RPM fluctuations of a single cylinder4 stroke engine(acceleration during power stroke, and deceleration during other 3 cycles) is what causes the flicker.

Caps added to the field diode output, will filter the rough half wave rectified DC into a flatter DC voltage, which will clean up the AC output waveform.  It will also increase the voltage output a little, but will have no significant effect on flicker, because the source(z winding) is still varying with the RPM pulses...

The only ways to get rid of flicker are to:
1.  Reduce or stop the RPM fluctuations, by adding cylinders, switching to a gas turbine or hydro as a prime mover.  Adding flywheel mass will reduce but not eliminate the pulses from a single.
2.  Add an AVR that will monitor the output and modulate the field input to electrically stabelize the voltage output and help tame the flicker.(most common modern solution)
3.  Add a cam and contacts to switch resistance in and out of the field circuit in conjunction with the power stroke to modulate the field input in conjunction with the power stroke to help
     tame flicker.(old school solution used by Onan and I suppose others)
4.  Use the generator output to make DC and either charge batteries or directly feed DC to an inverter, and use the flicker free inverter power.(Honda's solution used on EU series inverter/generators) 
« Last Edit: September 02, 2011, 03:44:08 PM by ronmar »
PS 6/1 - ST-5.