some of the st heads have horrible harmonic distortion, at least by modern standards
iirc the line is supposed to be better than 5% THD or no worse
seems like i have heard of some st heads being somewhere around 15+% THD
also some of the modern refrigerators are built to a price point, meaning the motors are no bigger
than they have to be to get by,, higher harmonic distortion results in more heating of the motors internals.
also if these are new units with electronic stuff, the distortion might be kicking their ass too, or
start caps can have issues with high distortion as well? maybe you lose a start cap and toast the start winding, or
lose a run cap and have other issues?
bottom line, maybe check the heads THD to see if it is really excessive for some reason?
excess heat can make the overtemp safty trip out to save the compressor motor, but this is not meant
to be a continous operation safety feature, so maybe it trips a few dozen times over a few days and when the
compressor cuts off you think it is normal shutoff and don't notice it is short cycling? if it cuts off and then cuts back
on too soon it can cause a start against high head pressure which will overload the motors start winding.
or maybe i am all wet? wouldn't be the first time!
reaching at straws here, seems like if you got anywhere from about 110-128volts and 58-62hz or so, steady and reliably
especially at startup, maybe you gotta look at THD as maybe causing issues? perhaps checking the voltage droop
on startup to make sure you don't have a huge spike that the gen can't service and the voltage drops too far making
the unit unable to come off the start windings as soon as it should?
bob g