I'm not talking about high freq fuzz like I see with SMPS on AC input and radiating out. I'm talking about "NOISY" distorted, lumpy sinewave from ST with bit of spikes on it.
I know. But still doubt that's the cause of the problem. A noisy waveform as you describe is caused by high frequency (>60 Hz) content. And, as I mentioned, you may see it in the voltage waveform, but I have my doubts about whether it shows up much in the current waveform of an inductive motor.
What kind of flywheel did you use in that case?
Good Q - I'm ASSUMING the OP has a Listeroid, which AFAIK tend to have too-light flywheels for use as AC generator prime movers.
And I do understand now what you mean by the freq variations around 11Hz cycle.
Good. Allow me to take the next step and show why I think this is the root cause of the toasted compressors...
Let me make a few simplifying assumptions...
Imagine the AC load (the refrigerator motor in this case) draws 4A rms from an ideal 60 Hz source.
Now, imagine that the internals of the motor present resistive losses of, say, 5 ohms. In that case, it's easy to see the resistive losses would account for 80 Watts (twinkle twinkle little star, power equals I squared R, right?)
Now, let's assume the Listeroid freq and voltage vary so wildly that the motor only does
work for 1/2 of the time with the other half of the time spent decelerating, or slowing down, as the engine coasts down in speed after the power stroke. If it's required to do the same total average work (as I suppose it would in this case), you'll probably agree it needs to work twice as hard in the first part of the cycle, and then loafs along for the 2nd half, right?
Now, let's go on to assume that when the motor is doing twice the work, it draws twice the current. (It's a stretch, but not
too far from reality). So our motor draws twice the current for half the time. And let's go on a bit more, and say that during the 2nd half of the cycle, where the motor is coasting, it draws zero current.The average current would still be our original 4A rms, right? It would draw 8A for a bit, then 0A for the next bit, and the average works out to 4A. So no big deal, eh?
But wait. What about our resistive losses? We now have I^2R losses of 320W for 1/2 of the time and 0W for the other half. And the average losses are now 160W. Yep - same average value, but the losses have doubled.
Is the reality exactly like this, where the motor losses double? No. But I'd argue they
do increase. And increased losses mean more heat. And that leads to toasted compressors...