if everything else is equal, a generator with a pf of 0.8 will be a better unit for mixed loads
than one with a pf of 1.0
there are a few notes that need to be made
when a generator is rated at a certain pf, it is rated to provide a certain amount of power without undue heating, or undue voltage drop, and maybe a couple of other factors like distortion or exceeding field current etc.
there will be examples where another genhead might do better even though technically by spec it shouldn't, however if you measure everything you will generally find it is running hotter than spec, or the voltage is drooping under spec, field current it running higher or the distortion is getting over spec's, or something else.
so what does this come down to ?
for example
given two genheads, genhead A rated at 6kwatts at pf 1.0 vs. genhead B rated at 6kwatts at pf 0.8 my money would be on genhead B.
the reason being genhead B can deliver all of its rated 6 kwatts into a mixed load with a pf of at least 0.8, while genhead A cannot deliver its full rated 6kwatts into the same load
usually we find that generators that are rated at pf of unity or 1.0 are meant to power resistive loads and are referred to as light plants... if they are not referred to as light plants it is left to the user to understand that the unit will not deliver full output into a mixed load.
even if the unit appears to be able to drive a mixed load up to the nameplate rating, the unit will likely overheat and die a premature death.
probably ran around the block on this one, power factor and its correction has been a topic that i have long had a real interest in. this topic is very hard to get good answers on, and often you can get all sorts of answers even from EE on this topic.
my favorite answer is "why do you care, you aren't charged for poor power factor by the power company?" usually i get a big blank stare or silence when my response is "but i am the power company dammit"
for a better explanation on the topic of power factor and power factor correction, written by an EE with years of experience working for a utility company and also an avid DIY'er, that is presented in such a manner that most normal people can understand it, i would suggest Bill Rogers book.. it can be found at Utterpower.com the book was out of stock for some time, but my understanding is it is back in stock.
i cannot over promote this book!
it is my opinion that any serious diy'er should avail himself of information on power factor, he ought to get a firm grip on the concept and understand what exactly it is and how to correct it as needed.
because we as diy'ers don't generally overbuild their gensets to the point that they have tons of excess capacity, for a plethora of reasons that most know all too well. Because we build gensets that are generally a bit smaller than we would like, means we need to manage our loads. a significant part of management is power factor!
why build a genset that is for instance 10 kwatts with a pf of 1.0 and find we cannot power much more than 8kwatts of load without overheating the generator or having too large a voltage drop? why do this when we could educate ourselves on power factor and its correction and get better utilization of the 10 kwatt rating? getting to a pf of .95 will allow the same genset to deliver 9500watts without overheating or badly drooping voltage.
i could go on, this is afterall a favorite topic with me
hopefully this will help