I would like to detail my in-process Lister type installation with the purpose of exposing flaws and possible failure points. I am preparing to run the system for extended periods. This will also serve as a test for what is possible of an engine run straight from the factory. Blast away, I have a thick skin.
I live in southern Connecticut and the reason I am involved with these engines is to net meter with the utility. The utility is onboard and I am in the final approval process. I did receive resistance when I went to my city for my electrical permit. After a bit of educating they gave me the go ahead. The primary concerns the city had were with noise and possible odors. The regs state that the noise level can not exceed 55db measured one foot beyond my property line during daytime hours (8am-8pm) the allowable noise level is reduced to 45db at night.
I have a 12/1 and 6/1 power line brand.
The generator is installed in a free standing one car garage that is only about 30 feet from the property line. The 12/1 at 1000rpm was just too loud to run for extended periods, it was so loud that I got a call from a neighbor complaining about the noise.
Issue # 1 noise levels:
I have a generic auto muffler and down stream the exhaust flows into a buried 30-35 gallon steel drum. The noise level using this setup on the 6/1 @ 650rpm is about 60db when loaded to 3500 watts. If I drop the rpm to about 525 the db with a 2100 watt load the level drops to 55db. I think with some sound dampening in the garage I could drop the db level further. I am considering Homosote, but at about $24 per sheet this is not a cheap option. Based on the research I have done plain sheet rock, even in multiple layers, offers little sound reduction. If anyone has other suggestions I am all ears.
Issue #2 Safety
Assuming I can reduce db to an acceptable level and I have enough free WVO, I could conceivably run the engine 24/7. If I do run for long periods I would like to run the engine at a lower rpm, 450-500 is what I am targeting. I have a pulley on the way for this speed. I need to feel confident running the generator unattended, for that I need some safety controls built in.
I would like to have automatic shut downs that activate on:
Over temp
Over speed
Low oil
The sensors for these are available in one form or another. What I have not been able to find is the mechanical actuator that would be used to shut off fuel and or air. I envision each sensor with its own relay all connected to 2 common shut off devices. One would be the fuel cut off and the other would be the air cut off, so any of the sensors could cause a shut down. I would like the actuator to turn off when electricity is cut off, i.e. a spring would be countered with an electromagnet which allows the fuel or air to flow, and when the electromagnet is off the spring would shut off the fuel or air. Perhaps there is a fuel solenoid available that has a normal position of off that when energized it will open? All suggestions are welcome.
Issue #3 lube Oil
If I run this engine for long periods I need to make sure it has clean oil. A bypass filter will also allow fol extended oil changes and open up the possibility of using detergent oil. I am thinking of adding a bypass filter to the system in addition to the standard full flow spin on filter. I have a good idea of the filter I want to use, but I do not want to use the onboard pump, because I think the pressure is too low and I would rather not have to cut into the existing plumbing. I envision adding a pipe to the oil drain hole which will lead to a small electric pump. I would like suggestions on what pump to use and weather I should put the pump before (to push oil through the filter) or after the filter (to pull oil through) I will have pressure gauges before and after to indicate when to change the filter media. The filtered oil will be pumped into the hole next to the compression release valve, as others have done. I may add a thermal sensor that would activate the oil pump when the oil temp is above 80-90f if I find it can not handle cold oil. Does anyone have suggestions on pumps that may work?
Hotater I believe you have the most experience with long run times, do have any advise on what to look out for, or any suggested procedures or systems?
Best regards
Scott