This post brings to mind a question I've had on a SOM. Do these things sense a load and start with the load attached? Do they then shut off when the load goes away? Seems it would be hard on the engine to start and run a load while cold, then perhaps shut down shortly thereafter. A run on timer would make more sense. At least get the engine up to some temperature, apply the load, and stay running for some time. I would think a four fold approach would make more sense, a remote switch to start the run sequence, a timer to start at a preset time, a voltage dropout senser to monitor the grid power, and a local start sequence for maintenance testing. Each could be interlocked and switched in and out as needed, but each would start a series of events leading up to power switching in.
In my mind an automatic start should monitor at least the oil level, oil pressure if oil is pumped, water temperature, RPM, temperature in the generator, fuel level, output voltage, output current, and position of breakers. If anything goes wrong, the system should latch an indicator telling me what to check and then shut down. With these engines that need a daily drop of oil or dab of grease, unattended start seems to be something that might lead to neglect.
To me, my Lister is more of a backup to my backup, if the primary power system fails then the Wisconsin starts and takes over, if that is off line for whatever reason then it is time to go to the lister and start it up and manually switch it in.