« on: April 26, 2009, 02:47:56 PM »
Hi,
Correct on 1 and 2.
Let me address the breaker size first. 120V * 35A = 4200watts. Well under the 5kW rating of the generator, so it's fine that way.
The other thing the breaker has to be sized for, believe it or not, is the engine. Simply put, there is no point in having a 35A breaker if your engine cant pump out enough power to make the 35+A required to trip that breaker. In most commmerical generators, the engine is sized above that of the generator, that is you might have a 30kW engine on a 25kW generator end. In the case of some (?most?) listeroid applications, we have a generator end thats sized larger than the engine.
The way I determine the breaker size for the engine
1) Engine at operating temperature, everything as it would be if you weren't there; genshed closed etc.
2) Slowly load the generator up
3) Watch the amp meter(s) as you load up the engine
4) Dont go over the generators rating (in this case 5kW or 41.666A @ 120V)
You will hit a point where you have either overloaded the engine (black smoke or belt slip or rack full open or overheating or a sense of "that's enough"), or the generator, and you need to size the breaker BELOW that point. For exaple, if your engine holds 30A nicely, but is pumping out black soot at 35A, size the breaker at 30A. Remeber that breakers dont drip exactly where they are rated. Most need a 25% overlaod to trip within 1 minute. This all depends on exactly how much power you can get out of your engine, which we know can vary greatly.
As for the ground, you can improve it by using ground plates, same idea as a ground rod, only they are about the size of a dinner plate, and they get buried instead of driven in to the ground. They have a large surface area, so they can get a better ground where you cant drive a rod deep enough.
The point where you tie the neutral bus to ground is called the BONDING point, this has to be a good connection for the system to work properly. I wont bother explaining all the things that can go wrong if it's not, so just make sure it's good. Only do this at one point! If you bond in the main panel, dont think you are improving things by bonding at the generator as well! I'll skip the technical explanation on why this is so.
One thing to note here, only ground at ONE place. If you ground everything at the genshed, dont put ground rods in at the panel that's 100ft away, instead tie everything back to the ground rods at the genshed. It's ok to have mutiple plates/rods at one location, but they should all be tied in with one piece of wire. Again, I'll skip the technical explanation.
OK, hypothetical situation; so you have grounded in 1 place, and bonded in 1 place. The connections are all good, but the earth is so dry that your ground is lousy. Lets pretend we have a loose "hot" wire in a 3 prong metal case (grounded) drill. Three possible things can happen.
1) Loose wire touches a neutral wire inside the drill, big spark, current flows back along netural wire, and the breaker trips. This would not trip a GFCI.
2) Loose wire touches the metal case, big spark, current flows back on the ground wire, to the bonding point, then back on the neutral wire to the generator, and the breaker trips. If you were on a GFCI, it would also trip (likely before the breaker), as this is a "ground fault".
3)You set the drill down on a 2 by 4, and the loose wire hangs out of the drill, and makes contact with the ground, but the drill stays off the ground. Not much current flows, because of the high resistance of the bad ground, and the drills distance from it. So, maybe the breaker doesn't trip, because not enough current is flowing. This is when you thank yourself for buying a GFCI outlet or breaker, as that has just tripped, because all it needs is something like 0.015A of ground current to trip.
The point of the story is that even with a bad ground, situation 1&2 take care of themselves, as no current ever went thru the ground rods. Situation 3 might not take care of itself, even with a "good" ground, and that's why GFCIs are important, but even more so when you have a bad ground.
Sorry for the lecture.