So how may amps can I pull on single phase zig zag 120/240 V, the gen head plate says 30 amps at 3 phase, is that 10 amps per phase x 3 = 30 or 30 per phase?

Thanks Larry Harter

2
Thanks Gary, Please refresh my memory, if my generator was rated at 10KW 3 phase, how much less would it be on double delta 120/240 single phase, how many amps per leg?

Larry Harter

3
Back in 2007 I got a used TR2 10KW 12 lead Lima marathon 3 phase generator from dieselgman, rebuilt the top end and rewired it to zig zag for 120/240 single phase.
Last week had a 66 hour run from the Ice storm, in Western Washington.  It wet stacked towards the end, not loaded enough, so have been doing some searches and found the double delta schematic for single phase. Would that be any better than zig zag for loading.
Thanks Larry Harter