Author Topic: The Listeroid Chronicles-WMO and Other Listeroid Modifications  (Read 291350 times)
Re: The Listeroid Chronicles-WMO and Other Listeroid Modifications
« Reply #735 on: January 28, 2019, 08:10:06 AM »
Hi Guys, I have wondered about trying to build an SOM out of my CS. Bruce has done a wonderful job of automating his with compressed air. I am reasonably well acquainted with the original electro/mechanical relay set up. I think a PLC might well be used to detect a power outage and then kick in the generator. The problem we have here is automatic breakers on the grid, when the power goes out the breakers try to re establish the grid several times over about 30 seconds. Could a PLC be programmed to allow for this and would it detect when the power comes back on, stop the generator and switch back to the grid? How much paper work would be required to get approval for such a system from the electricity distribution companies?
Might be easier to just go and crank the handle and flick the cross over switch. I can always hook up a single light bulb to the grid to tell me when it comes back on. Please bear in mind that I have a fully functional ST2 SOM so I could theoretically go off grid tomorrow. The whole purpose of the CS 6/1 and ST5 head was to ensure reliability and avoid anything electronic.
EdDee
« Reply #736 on: January 28, 2019, 11:01:09 AM »
Hi Bob,
As to mains outage detection and timing it so that intermittent starts and farts on your power line...quite easy with the facilities the plc's normally provide... But, as Bruce mentioned, more often the mechanical aspects of the project can be a bit daunting - 24v Electric start with a good torquey starter motor would be the way to go here... No need to worry about decompressor as such... The rest are fairly simple things, the rack closer would be quite easy, temp measurements and the rest fairly simple, industrial lego bits could be used.... The trick would be to get the unit stable mechanically and electrically, ie starts and stops at the turn of a key... To retrofit on top of that would be first prize!!
Also, as mentioned many times before, once the basics are taken care of, they become a fallback in the event of a malfunction further down the line ... (Operator or Mechanical...)
Ed
« Reply #737 on: January 28, 2019, 02:58:08 PM »
Yep, a starter that can crank though compression would simplify things, though a decompressor can stop even a crankcase oil runaway.  Either way, a PLC could do the controller job.
Electric linear actuators could easily replace the two air cylinder ones I used for rack closer (needs 10+ lbs force to overcome governor springs) and valve lifter. My lifter is active and actually lifts the valve, unlike the SOM which just inserts a spacer so must be applied on shut down or the next start would fail at compression.  I had massive force available via $14 air cylinder. A well designed spacer method for the valve lifter is very low force, an RC servo could do it.
« Reply #738 on: January 28, 2019, 09:27:32 PM »
It would be really easy if I could get my hands on one of these: https://www.youtube.com/watch?v=7fhhHdrylRA
« Reply #739 on: January 28, 2019, 09:39:18 PM »
Yes, those starter-alternators are a sweet solution.
The ST heads could be electronically driven as motor, by driving the stator and field coils appropriately ala an inverter, then switched over to become an alternator.   Given the QC problems I've seen, and variations between units, I don't want to waste the time developing anything for them, until/unless some savy importer gets serious about improving their quality.
« Reply #740 on: January 28, 2019, 09:46:07 PM »
Hi Bruce, here`s a video showing how the original CS 8/1 worked: https://www.youtube.com/watch?v=ecEwlAmcWrU
« Reply #741 on: January 28, 2019, 09:52:29 PM »
The massive solenoid for rack and exhaust decompression valve action would be near impossible to duplicate with off the shelf components, i think.  No solenoids near that size.
A small linear motor-actuator for the rack closer and a solenoid or RC servo for the valve spacer would do it, though.
« Reply #742 on: January 28, 2019, 10:29:23 PM »
They definitely built stuff to last. I might have a word with Rob at Old Timer Engines in Queensland, I know he buys a lot of old CS engines and has a large collection of used parts. He could probably source original SOM parts. Probably cost me a small fortune, so your approach is probably a better bet.
EdDee
« Reply #743 on: February 18, 2019, 02:44:26 PM »
Hey Guys....
And now for something completely different....Generators/Solar/PLC's and why would I run them together...
To cut a long story short, or maybe not so short, well let's see how it pans out...
This past weekend, we actually had a SCHEDULED power outage...Advertised well in advance, blackout areas clearly designated, times clearly stipulated, real first world stuff... Something that's new to me!!
This actually allowed me to do "first parade" on my gensets getting them ready for the scheduled power drop, another thing that was new to me, time to do the walk-round and kick the tyres before turning the key....
At the scheduled time, 06H30, lordy-be....The power went out as it was supposed to. The auto-start kicked in as it was supposed to, somebody went to the thumpmonster and turned the switch as they were supposed to, it started up as it was supposed to, the auto-start shut down as it was supposed to, thumpmonster took the load as it was supposed to, all was happy in Darkest Afrique.... Or was it?
Well here is where things got interesting... Nothing broke down, nothing stopped turning, nothing stopped working... Everything was just too good to be true..... This kept going until I started meandering around the place, the devil finds work...etc...etc...etc....
So I started looking at power graphs and what was happening on my own little local grid. Solar was taking care of 95% of the demand, thumpmonster taking over for the 5% that was "out of design scope" for the solar.... Here I was running 10Kw of availability, split 50/50 solar and dino, with the free stuff doing most of the work. The problem is/was, the solar is upsy downsy with intermittant clouds, dino takes over for a few minutes, then demon dino just sits there spin-waiting for another cloud... Long enough to shut down for, but a right PITA to run and start up every hour or so for a few minutes....
What could I do? At the time...Nothing...Just let Demon-Dino spin thumpmonster till he was needed, a grand total of about 10 to 12 times during the day (Power came on around 19h30 or so), after looking at the graphs I could draw from the solar setup.
A solution: I have an old Siemens LOGO plc lying around, 6xdigi inputs, 4xdigi outputs....
After a bit of keyboard bashing, I came up with a little idea/package that will do as follows...
Add 2x220v coil relays on the mains circuits to and from the autostart gennie to see where there's power.
Add 1x24v coil relay on an output of the LOGO to enable the autostart facility of the gennie.
Add 3x Buttons to the PLC to allow some finger poking to do things.
Add a couple of idiot lights to show whats's doing's whats's...
Drop some keyboard time into the PLC and away we go...
The Plan:
Connect a 220v coil relay across the mains input power to the gennie, if the contacts are in the closed position, there's 220v Present.
Connect a 220v coil relay across the mains output power from the gennie, if the contacts are in the closed position, there's 220v Output Present.
Connect the "LOW BATTERY" warning contacts on the inverter to the PLC on a digital input.
Connect a 24v Coil relay to one of the PLC Outputs.
What the software does:
It looks for mains in, mains out around the gennie, and NO low battery signal from the Inverter
If power input drops, the PLC monitors the solar inverter for a low battery signal.
If a low battery signal occurs, the PLC signals the gennie to start, if the gennie doesnt start withing a prescribed time and present a 220v output to the PLC, an alarm is raised(siren/flashing lights/whatever) and the start is aborted.
If the gennie starts successfully within the preset time, the plc holds it on until the low battery signal is cleared and then for a further preset time(minimum run time I can decide on after installation)
This carries on ad infinitum, until mains utility power is restored.
The button functions are:
Alarm Clear and Restart
Disable
Enable
Idiot Light outputs are:
Control Disabled
Fault
Ran the logic through the simulator, added an additional timer for mains detection, the mains has to be on and stable for a preset time(30sec currently) for it to be recognized... This stops the gennie from shutting down on a mains impulse... Also added the facility for when mains output drops from the gennie for the preset start timer, the gennie doesn't try and restart, but fault sirens etc are triggered....Let's face it, if a diesel stops, its for a damn good reason....(Also, additional sensors can be added to this line if I want to...Low oil, overheat, low fuel....)
And that's about it!
Wonder if it will work?
Time to go and attack the junk pile for some bits and bobs...
Keep it Switching...
Ed
« Reply #744 on: February 18, 2019, 04:11:55 PM »
Nice work, Ed! That should do a nice job of keeping the genny from idling.
« Reply #745 on: February 18, 2019, 08:19:50 PM »
2 changes.
a)  Set Grid Valid to be 2 minutes.   Generator is already running, you want the grid nice and stable when you switch over
b)  any way to have generator run for a 3 minute cool down, before shutdown ?   Gives the alternator windings a chance to get cooled by the fan airflow, lets the engine cool some before killing the system.
EdDee
« Reply #746 on: February 19, 2019, 08:36:44 AM »
Hi Mike,
Those two delays are catered for, I agree that they seem a bit short, but in practicality, the gen will shut down as soon as it's mains input is at 220, built in feature that I have no control over. The shutdown and startup delay are more for when the power is out and batteries run low, allowing the gen unit a little grace and cooling... Unfortunately, the little Logo Plc I am using is way short on programming space, not enough space left to add the instructions to control a pre-gen isolating contactor, otherwise I would put it in...(I simply linked idiot lights to the available outputs, that takes buggerall mem and I got away with the few extra links, but barely.)
Only discovered this quirk with the gennie quite late yesterday evening when I was going over the final bits before I attack the junk pile... I can rewire the gennie to make it totally plc dependent, but prefer to keep it standard and capable of non-managed self operation should the plc fry....
No doubt I will probably find some additional "quirks" with the chinesium assembly of the panel before this little bugger is installed...
Ed
EdDee
« Reply #747 on: February 19, 2019, 08:53:58 AM »
Hey Glort,
Grid tie inverter and gennie shouldn't be a problem, as long as you have a GTI that is capable of sensing feedback into your prime system and further capable of regulating its output that the actual GT feedback is 0, or near 0 power... The windings on a gen are only capable of supporting its rated load - If you are trying to push 20Kw into a little 2Kw gen, back up its line, unfortunately the smoke escapes from the little copper fuel pipes in the spinny bits, and never quite makes its way to filling the tank!
There are GTI's out there with directional current sensing - ie it senses how much power is flowing into your household and then turns up the wick until the power flow is balanced between consumption and creation - if power consumption goes up, it opens its taps a little more, converse for when its going down. These GTI's are fairly common where power meters are incapable of back winding, or where "covert" installations are done, where municipalities don't cater for or don't want consumers to back feed the grid.
Incidentally, these things are basically what I would call solid state "induction generators"  - No grid frequency to clock to, no power generation.....
I wouldn't run more than one of these GTI units on a prime gennie or inverter, the chances of feedback oscillation/cycling would be a bit worrying... Also, probably the cheapest chinesium genset would give a considerably better waveform than a pseudo-sine wave inverter as a prime... Square edges and spikey bits on what should be a clean sine wave for your GTI would defs upset the applecart a bit for your GTI to clock to.....
C'mon pal, you're the chip oil king around here...bugger the solar cr@p, sync a few small gensets together and run the neighborhood!!
Cheerz
Ed
« Reply #748 on: February 19, 2019, 05:00:40 PM »
Ed raises a good point about the potential issue of GTI compatibility with a high THD and spiky sine source.  It's yet another gotcha.  I don't think I'd be willing to risk both GTI and generator head on such an experiment, though I'd love to watch. :)
EdDee
« Reply #749 on: February 19, 2019, 07:59:53 PM »
Continuing the saga of "And now for Something Completely Different".... Otherwise known as "PLC's, Auto Start Generators and Inverters, Getting them to play nicely!"
Here is a link to the Logo Software - Demo version, fully functional with simulator et al, just cannot download a project to a PLC:
https://w3.siemens.com/mcms/programmable-logic-controller/en/logic-module-logo/demo-software/pages/default.aspx#Demo_20software
and attached hereto is the little proggie I wrote... in zip format... The umpteenth revision thereof, shoehorned into the few memory places the little Logo has, with a few extra features I managed to include after hacking out a few things and changing some push buttons to SPST switches, allowing me to add a little more useful logic into it....
Basic info needed to run this thru the simulator is (a little imagination required here chaps):
Genset:
The genset will autostart if mains power drops away from the mains input, it will continue running until mains power re presents itself again.
The genset can be switched from auto-start to manual mode, this is what I will use to turn the gennie on with by using a plc output/relay instead of turning an ignition key.
The inverter has a single "Normally Open" contact that will close on low battery, remaining closed until the battery level is back up to a predefined preset.
Things are pretty much connected in a straight stripe -
Mains in -> Mains Sensing Relay -> Mains Input Isolating Contactor -> Genset Proper -> Mains Output Sensing relay -> Inverter/Solar Mains Input -> Inverter -> Inverter Output to the rest of the DB Board
For mains sensing relays, there is simply 220v on the coil of a relay...If the 220v buggers off, the relay goes to open state, the plc picks this up and responds accordingly.
As far as controls go, there are only three -
A start Fault reset - If the gennie doesn't start within the preset time, start and further operation is aborted.
Enable System - When this is off, the gennie will not start or run, unless it is switched to manual on the gennie itself.
Isolate Mains input to gennie - When off, the mains input into the gennie is....well ...not there.....
Indicators and Idiot Lights:
Controller Enabled
Start Fault
Relays/Contactors:
One relay to sense power from the mains.
One relay to sense power out the ass end of the gennie.(when mains is present, and the gennie isn't running, the mains power is bridged through the gennie automatically as one of its internal functions)
One relay to control the auto start feature on the Gennie
One Contactor to make the mains input to the gennie... be.... uhhh ....not there...
If you get around to running the sim, Its quite a bit of fun, if you're into this sort of thing, set all the inputs and outputs and watch what happens when you present a myriad of thing to my little proggie that I never thought about... Break it and tell me how you did, so I can make it idio....sorry, operator proof!
Have fun!!
(And should you find this proggie useful, please do not hesitate to send me a pint via email!)
Keep it switching...
Ed
« Last Edit: February 19, 2019, 08:27:21 PM by EdDee »