I finally got it figured out.... :)  After looking at this page at Utterpower.com: http://utterpower.com/genhead.htm, I found that my 4 wire gen-head was factory wired for 240V. I was ony pulling 50 amps on one 120V leg.

After switching a couple of wires to the voltage regulator and strapping the leads together, I now have 120V at the full 100 amps.  ;D

I should now be better prepared to understand the ST genhead mated to the Listeroid that I will be purchasing very soon....  ;)  I plan on having the Listeroid run my 220V airconditioning load using biodiesel next summer. Shoud be interesting...   :)
« Last Edit: November 30, 2006, 01:02:39 AM by Technonut »
Metro 6/1 (4 kW Indian GenHead)

GM-90 6/1 (7.5 kW ST GenHead)

Isuzu 3LD1 (12.5 kW Croatian GenHead)

biobill

  • Sr. Member
  • ****
  • Posts: 408
  • 'riods make good houseguests if fed right
    • View Profile
Re: Indian Head to 110v only???
« Reply #16 on: December 02, 2006, 04:47:05 PM »
  Got a used 480/240X240/120 3kva transformer off the web. Problem solved.  Thanks for all your info and input.